Hi running off grid with 2 pylotech batterys. all working fine but i have purchased a generator 6kva but the inverter will not close on relay 1 to caharge batterys. changed settings but still no joy
Check your incoming frequency. It may be out of range of accepted frequency
Which firmware version is the Multi running?
The latest v1.11.
Then with the latest VictronConnect (v5.80) you should be able to see settings for generator support.
Moderate generator load changes under General settings:
Then under the Grid settings page there should be an option for UPS function.
Turn this off if the Multi is rejecting the generator after some seconds. This does increase the transfer time though:
i have v 1.11 on rs
and v 5.80
Additional resources still need to be added for this topic
GX - Generator auto start/stop