question

david-barkley avatar image
david-barkley asked

rs 6000 48 volt 100 450 a

Hi running off grid with 2 pylotech batterys. all working fine but i have purchased a generator 6kva but the inverter will not close on relay 1 to caharge batterys. changed settings but still no joy

Generator
2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image Alexandra ♦ commented ·

@david barkley

Check your incoming frequency. It may be out of range of accepted frequency

0 Likes 0 ·
Show more comments
1 Answer
wkirby avatar image
wkirby answered ·

Which firmware version is the Multi running?
The latest v1.11.
Then with the latest VictronConnect (v5.80) you should be able to see settings for generator support.
Moderate generator load changes under General settings:
1673288027109.png

Then under the Grid settings page there should be an option for UPS function.
Turn this off if the Multi is rejecting the generator after some seconds. This does increase the transfer time though:

1673288437375.png




1673288027109.png (32.1 KiB)
1673288437375.png (36.1 KiB)
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

david-barkley avatar image david-barkley commented ·
thankyou i will try this setting.

i have v 1.11 on rs

and v 5.80

0 Likes 0 ·