I am considering buying the 250/70 Smart Solar..1 version is the TR--screw terminal +/- and the other has 2 x MC4 inputs
Question is do the 2 x MC4 inputs connect to 2 individual MPPT's OR just combined into one MPPT internally ?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
I am considering buying the 250/70 Smart Solar..1 version is the TR--screw terminal +/- and the other has 2 x MC4 inputs
Question is do the 2 x MC4 inputs connect to 2 individual MPPT's OR just combined into one MPPT internally ?
As you suspect, the 2 pairs of mc4 connectors are combined in the mppt to a single tracker.
Pls note, each pair of mc4 are rated at 30a.
Thankyou...It will make me re think my design of having 12 panels in a row with 2 strings....especially as at the end of the panel array there is often shading which with only 1 tracker will reduce the entire array's out put significantly...
do all of Victrons MPPT 's--smart and blue configured the same--ie only one MPPT internal tracker arther than multiples ?
The SmartSolar MPPT RS solar range have multiple mppt trackers.
The 450/100 has 2 trackers, and the 450/200 has 4 trackers.
Hi @Garry414
If you have selective shading on one panel in a string then all the panels in that string get their Amps reduced. Regardless of the number of trackers. This is the issue you need to address. Multiple trackers may have little effect at all on overall output.