I have 12 used agm batteries that I want to configure to a single 24v batterybank. How would you wire this in the best way? Do I need balancers? If yes, how many?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
I have 12 used agm batteries that I want to configure to a single 24v batterybank. How would you wire this in the best way? Do I need balancers? If yes, how many?
Easy to answer: put 6 batteries parallel and the 2 groups of 6 in series then you get 24v system.
agm batteries need no balancer
Balancers would be good here. And long strings of six batteries is likely to cause imbalance, even if tapped at opposite ends of the strings or connected with busbars. It's not true that AGMs don't go out of balance, although long periods on float and low currents mean self balancing is likely.
Four strings of three in parallel would be much better.
I totally forgot this thread and didn't get any notifications.
Now almost one year later I have had some imbalanced in my bank, 2 stings in 6p2s config.
I have had these disconnected and measured individually because the two 12v strings had 1.2V difference during charge and rest. Now they are pretty much okay again after some switching around.
My questions is: Why would 4 strings of 3 in parallel be better than all six in parallel?
Right now I'm thinking about wiring these in 2s6p instead. The disadvantage of this as I see it is that I will need more sensors to monitor each 24v string. Currently I only need two sensors for each 6p string. And I can easily see the difference in voltage. Also I have heard that the advantage of parallel batteries is that they balance themselves? That was the main reason why I had them wired all in parallel. But now I'm unsure, also I have gotten my hands on more of these batteries and it would need less cables to wire these in series first.
Any thoughts?
2s6p vs 6p2s?
You have used batteries. Good chance of very different states of charge. And wear. Make sure all fully/equally charged before connecting.
completely agree, you can also check each battery separately with a multimeter to ensure there all within 0.1v of each other.
section 3.4
https://www.victronenergy.com/upload/documents/Wiring-Unlimited-EN.pdf
Totaly different situation, but the victron battery balancer (2pcs) do their job very good balancing my 2s2p setup on 24V. Added temperature probe to each battery, (yes it occupies the whole Cerbo temp inputs) and i have not a single issue, battery's are from the same production date though. (VMF Greensystems 105Ah) But i would like to see a balancer which can deliver more than 1A, since its really slow when there is an inbalance. If you wire the balancers to your digital inputs you can generate inbalance alarms by the balancer relay, which comes in handy.
Mabye this victron device would be better?