How do I wire 12 agm batteries to a 24v inverter?

I have 12 used agm batteries that I want to configure to a single 24v batterybank. How would you wire this in the best way? Do I need balancers? If yes, how many?

AGM BatteryBattery Balancer
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

4 Answers
klim8skeptic avatar image
klim8skeptic answered ·

You might want to look at Wiring Unlimited for some ideas.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

khschmidt avatar image
khschmidt answered ·

Easy to answer: put 6 batteries parallel and the 2 groups of 6 in series then you get 24v system.

agm batteries need no balancer

13 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

kevgermany avatar image kevgermany ♦♦ commented ·

Balancers would be good here. And long strings of six batteries is likely to cause imbalance, even if tapped at opposite ends of the strings or connected with busbars. It's not true that AGMs don't go out of balance, although long periods on float and low currents mean self balancing is likely.

Four strings of three in parallel would be much better.


1 Like 1 ·
Show more comments
klim8skeptic avatar image klim8skeptic ♦ commented ·
@K.H.Schmidt l think you have just made a 72v battery?
0 Likes 0 ·
sharpener avatar image sharpener commented ·

Don't think so! Also worth taking the + and - leads from opposite ends of each bank of six so as to more or less equalise the currents at each battery as this will even out the wear.

0 Likes 0 ·
kevgermany avatar image
kevgermany answered ·

You have used batteries. Good chance of very different states of charge. And wear. Make sure all fully/equally charged before connecting.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

nesswill avatar image nesswill commented ·

completely agree, you can also check each battery separately with a multimeter to ensure there all within 0.1v of each other.

section 3.4

https://www.victronenergy.com/upload/documents/Wiring-Unlimited-EN.pdf

1 Like 1 ·
manta avatar image
manta answered ·

Totaly different situation, but the victron battery balancer (2pcs) do their job very good balancing my 2s2p setup on 24V. Added temperature probe to each battery, (yes it occupies the whole Cerbo temp inputs) and i have not a single issue, battery's are from the same production date though. (VMF Greensystems 105Ah) But i would like to see a balancer which can deliver more than 1A, since its really slow when there is an inbalance. If you wire the balancers to your digital inputs you can generate inbalance alarms by the balancer relay, which comes in handy.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

mattie avatar image mattie commented ·
I had a HA01 to balance the two strings I had. But it melted in the end. It's optimizong current is rated to 0-5amps.. However probably just a cheap product that I won't dare to try again even tho many have had success with it. But Im guessing that they worked in the beginning when the batteries were pretty close. After time they got worse making the balancer work 24/7 and heating it up.


Mabye this victron device would be better?