I want to be able to charge from 240 generator but have two multis in parallel for 4000k output. if in charger only mode will the problem of the parallel output be removed.
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
I want to be able to charge from 240 generator but have two multis in parallel for 4000k output. if in charger only mode will the problem of the parallel output be removed.
You did not say what voltage your Multiplus operate at. If they are the 120 volt versions then no you can not connect 240 volts to them regardless of mode.
Two 120 volt Multis in parallel would need 120 volts. You could step down the generator using a transformer.
Two 120 volt Multis in split-phase could accept 240 volts again by using a transformer to create two legs with a neutral from the center tap of the transformer. The legs would be 180 degrees out of phase. But you'd need your loads to be split phase also.
Switching between parallel and split phase requires reprogramming the Multis as well as rewiring all the AC inputs and outputs.
Your best approach would be to transform the generator output to 120 volts and feed that to the paralleled Multis
still trying to get some satisfaction from my pair of mulitplus 24 v 2000 w’s.
tried setting up in stand alone and connectEd the two hots from the 240 generator, one to each with a shared neutral, hoping to charge from my 12k Kohler generator. Still can only get one to go on at a time, one loads, as soon as other is ready they both click off. Charging ac in 15 amps, charging dc 40 amps.
seems like light load on generator but Kohler rep says it doesn’t have the umph, talked about kva32 max on generator. Thoughts?