Can 2 multiplus 2k be in parallel and accept 240 if in charger only mode?

I want to be able to charge from 240 generator but have two multis in parallel for 4000k output. if in charger only mode will the problem of the parallel output be removed.

multiplus in parallel
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Kevin Windrem avatar image
Kevin Windrem answered ·

You did not say what voltage your Multiplus operate at. If they are the 120 volt versions then no you can not connect 240 volts to them regardless of mode.

Two 120 volt Multis in parallel would need 120 volts. You could step down the generator using a transformer.

Two 120 volt Multis in split-phase could accept 240 volts again by using a transformer to create two legs with a neutral from the center tap of the transformer. The legs would be 180 degrees out of phase. But you'd need your loads to be split phase also.

Switching between parallel and split phase requires reprogramming the Multis as well as rewiring all the AC inputs and outputs.

6 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Leon schneiderman avatar image Leon schneiderman commented ·
Thank you Kevin. The generator has two 120 hot legs, one to each multiplus which are 120 volt. I believe they would be fine if programed for series but I would prefer to have access to 4000 watts. I believe I also could run them both as stand alone. But what I want is that 4000 watt capability mostly so neither 2000 watt unit has to handle an 1800 load. So my original ask is whether while in parallel with units set to charger only, if the output side where the two hots are united will not cause an out of phase shutdown of the charging cycle.