adding a second multiplus ii as a generator backup

I rarely would need to go over 5000w with one multiplus ii, but when i do need more power, could a second multiplus ii be wired into the generator input to add more wattage when needed, but not consume idle power when not needed, this should reduce ide power to only one inverter but allow for twice the power when needed. is this possible?

Multiplus-IIGeneratormultiple inverters
4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image Alexandra ♦ commented ·

@mfred68

I do want to clarify what you are asking here.

You want to power assist the generator output to provide more input power to an inverter that is running a load?

Are you planning on having a second battery bank?

0 Likes 0 ·
Show more comments
2 Answers
anieuwstadt avatar image
anieuwstadt answered ·

Can be done, but when there is more than one source of energy to charge the battery, the battery monitor internal to the "main" inverter/charger will not correctly track the battery's condition. If the battery does not have a BMS, add a SmartShunt and Cerbo GX to the system.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Michelle Konzack avatar image
Michelle Konzack answered ·

Yes, if you connect the backup MP to the ACin from the regular MP, the backup would be seen like a genset but make sure, that the output voltage of the backup is 2-5V higher then the standard one

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.