Hi, in my previous question I ask about the SmartShunt functionning. This additonnal equipement is here to help to understand what is the problem with my installation, but in fact doesn't help due to the low load on the Orion TR
More context:
-EasySolar 48/5000
-2 Orion TR48/XX now connected to the battery via the SmartShunt
-1 BYD B-Box Pro 10kWh (model from 2018, 4x2.5)
My problem is, I've seen my total input power for a period of time is much higher than my consumption and theoretically missing capacity in the battery. Here are 3 pictures of 3 days with Grid/Generator input + solar, with small consumption (the Orion output only drain few watts most of time and sometime near 200W but no more)


I've contacted EFT-System, the official BYD service company in Europe. But they only tell me "You are reading the data incorrectly. Adding those two values (solar + grid) does not give you the energy that has been charged into the battery. ". Nothing more...
This night (last picture) I've charged only with the generator, and this time I don't have to do any calculations. I've checked during the night, the battery has an input power between 1 and 1.15kWh. I start to charge when the battery was at 20% (I assumed 2kWh remaining). 
Someone here can help to understand this value? Is my battery defective?
Thank you :)
 
  These are cumulative figures, from the last time History was cleared, so allow for that. But these are indisputable, from the same device. These figures from my fla's, so not great efficiency charging the top 20% SOC daily. But I wear it, can't dispute it..
 These are cumulative figures, from the last time History was cleared, so allow for that. But these are indisputable, from the same device. These figures from my fla's, so not great efficiency charging the top 20% SOC daily. But I wear it, can't dispute it.. 

 The value isn't in decimal but it's more than 11 and 12. As you can see, with charging and only consumming power from genset, I used more than 1kWh++ from the genset that I used. (ATM, I've 4.6 from Genset and 3.9 for consumption). We can say that I've per day when charging a loss of 1kWh in the system. Maybe it's the same for the battery with higher loss... Very high ^^
The value isn't in decimal but it's more than 11 and 12. As you can see, with charging and only consumming power from genset, I used more than 1kWh++ from the genset that I used. (ATM, I've 4.6 from Genset and 3.9 for consumption). We can say that I've per day when charging a loss of 1kWh in the system. Maybe it's the same for the battery with higher loss... Very high ^^