mariusv asked

Victron Quattro 48/10000 and Pylontech US3000C added capacity

Hi,

Up until 2 days ago I had 4 Pylontech US3000C batteries and today I got 4 more so a total of 8 x Pylontech US3000C batteries are now used.

Do I need to change any settings on the inverter/Cerbro GX (somewhere) to make sure the system is using correctly all 8 batteries?


Thank you!

Pylontechquattro 10kva
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
klandos avatar image
klandos answered ·

No.

But Balance them! Easiest way bring all batteries to 100% for at least 8 hours. After that connect them in parallel, add the communication cables, double check dip switches and that’s it.

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

mariusv avatar image mariusv commented ·
@KLandos just checking to see if I got it right.

1. Connect all batteries using the plus and minus between eachother

2. Connect the link cables (let link0 free on the master)

3. Screw the earthing

4. Get the can cable on the master

5. Start the master which will start the all

6. Change inverter to ESS with Keep batteries charged

7. Done


I’m not sure what you mean by connecting them in parallel ?

0 Likes 0 ·
Show more comments
nickdb avatar image
nickdb answered ·

It is all clearly documented in the pylon install guide for the battery.

Just follow that.

You might want to update the “manual” capacity setting on the inverter, its good practice for in case the gx is unavailable.