What load capacity will I have with this solution

Morning everyone. Ive searched for an answer on this for a couple of days but not been able to find anything. Please can anyone tell me what kind of continuous KW discharge rate I can expect using a MultiPlus 2 48/5000/70-50, with my 7.6kw array, and with a 7kw PV inverter ( to handle my 2 strings) and the 5kva MultiPlus2 48/5000/70-50, along with two Pylontech-US5000 batteries (~9kwh), in a "grid parallel" setup, both when the grid is up and also what the continuous discharge rate is when theres a powercut?


During normal operation, when the loads are big and exceed the Multiplus2 capacity then I'm hoping in a grid parallel setup the mains grid will takeover to meet our surplus demand? Our peak loads in our house can reach 5 to 6kw in our house with 11kw max being reached when I did a test with all ovens, heat pump and appliances etc are going at same time, but generally 6kw would be our average peak loads for half an hour or so in evenings. My question is, when the grid is up and running, how much grid power will I be importing with our loads potentially reaching 6kw and what about our absolute max of 11kw or will my proposed solution meet most of those loads (assuming I have plenty of charge in my two batteries)? And the same question when there is a powercut?

What is the actual continuous kW discharge rate I can expect from my solution? And will I have a "power assist" ability where short peak load demands can be met and if so how much kW and for approximately how long, before the grid takes over?


Thank you for any help and info. I really appreciate it.

Matt

Multiplus-IIPylontechess discharginggrid parallel
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Jason - UK avatar image
Jason - UK answered ·

@matth76 I have a simular set up to what you have stated above. With the equipment ihave, my average power factor is 0.9 so my Multiplus II GX 5kva 48v runs constant at about 4.4kW. We have adjusted our energy usage to reduce the peak loads to below 5kW. In the event of a power cut, its no different, I would only get at most 4.4kW continuous. The only time my PV array supplements my loads when not charging my batteries is at weekends when I am at home or in the summer. I have a 5.7kW PV array. You can have a look at my VRM portal on the below link. In the photos is a schematic of my system as well.

https://vrm.victronenergy.com/installation/171934/share/db6807bb


2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

matth76 avatar image
matth76 answered ·

Thank you for your reply. If I got a third US5000 in the future would this raise the continuous discharge rate to even more than the 4.4kW, or is 4.4kW the maximum the Multiplus2 5000 can put out? Thanks again.

4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Jason - UK avatar image Jason - UK commented ·

@matth76 Officaly the max continuous output is 4kW. Adding more batteries will not increase the output of the inverter. The product data sheets provide the information you require.