Cannot change Multiplus 24/3000/70-50 Input Current Limit changed in Remote Controls

For the life of me, I can't figure out in VE Connect which value corresponds to changing the input current limit in the remote controls so I can increase this to 70amps on the input current limit.


Help?

screen-shot-2022-11-17-at-85338-am.png

current limitinput current
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Alexandra avatar image
Alexandra answered ·

@Allswell

It is in the name... 24/3000/70-50

70 refers to the DC max charging amps from grid. So what the inverter sends to the battery directly.

So 70ax24v= 1680W of battery charging max assuming no other restrictions and derating.

50 is the max AC input current. The max it will let in is 50A grid/generator input, some will charge the battery (to the max of 70A x battery voltage) the rest is for the 3000va loads the inverter can run.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

This ist the AC input current not the DC charging current.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

allswell avatar image allswell commented ·

Thank you Matthias. Yes, isn't the genset while it's charging the system the AC Input?