Since adding 2 Victron Smart MPPT's to my configuration, the Multiplus II GX just sits on Bulk

Since adding 2 Victron Smart MPPT's to my configuration, the Multiplus II GX just sits on Bulk. All was working fine before. You can see the SOC is over 20% (which is the floor set in the SMartShunt). Please help to get this working again so it goes into Inverter mode.


1668264930490.png

Multiplus-II
1668264930490.png (120.3 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
beattiemark avatar image
beattiemark answered ·

Here is a VRM snapshot with an AC load, the Multiplus-II should have switched to Inverter mode, it was OK before I added the 2 MPPT's ?


1668265502233.png


1668265502233.png (117.0 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

kevgermany avatar image
kevgermany answered ·

Could be a few things. Interesting that no current is shown going through the battery. Charge state may be incorrect, any idea when it last synched to 100%?

To start with

Check cabling correct, MPPTs should be connected to the load side of your shunt As should the multiplus.

What happens when AC in disconnected?

Are you using Bluetooth connections/smart network? This mix should, I think, use VE Direct Comms only.

Which GX device are you using?