question

johnone avatar image
johnone Suspended asked

Alternatives to Multiplus for domestic ESS

I'm one of the many currently jumping into installing ESS given energy prices/ want to be more sustainable. Attracted to Victron given sophisticated control via Cerbo GX and open source (we have RPi-based BMS). Kit now arrived - holy cow, the Multiplus II is one agricultural piece of metal. There's no wonder people on here occasionally mention the elephant in the room - noise. Buzzing, humming and the fan-on-steriods, all amplified by the steel box. The Multiplus II is not designed to be domestic kit. So, what are the alternatives - transformer-less, fan-less hybrid inverters designed for the domestic market which will talk to the neat Victron control units. Has anyone any experience of using other manufacturers' hybrid inverters with Victron control kit?

Multiplus-II
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

4 Answers
wkirby avatar image
wkirby answered ·

The Multi RS is a high frequency topology, light weight, powerful and quiet even at full chat.
However, ESS is not yet available and network approvals have not been attained for grid parallel operation. It works very well in standard mode, only connecting to the network to charge during off peak rates for example.

No third party hybrid inverters work with the CerboGX. You'd be very hard pressed to find a manufacturer who is willing to develop their systems to work with a competitors products one way or the other. PV inverters from other manufacturers do work, but Victron don't have any of these in their own lineup so no competition.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

johnone avatar image
johnone answered ·

1."ESS is not yet available" - Victron say (in numerous places): "the MultiPlus-II is the key component in a Victron ESS system"
2. "network approvals have not been attained" - less said about this the better!
3. "It works very well in standard mode, only connecting to the network to charge during off peak rates for example" - looking at the fine detail in ENA EREC G99, connecting a device which is capable of export (merely by changing settings) would seem to mean it would need DNO approval.

Back to the noise issue, we'll see how bad it is and have the fall-back of putting it in an attached garage. I'd prefer not to. Is it really the case that "No third party hybrid inverters work with the CerboGX"? Be in Victron's interests as it'll take some time for them to develop a hybrid inverter to compete with the many new Chinese models, which have gained Grid approval, and which are designed for the domestic market - put it in your hallway, that kind of thing.

9 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

nickdb avatar image nickdb ♦♦ commented ·
The newer ones post hq2225 have much quieter fans. I have them in my own home, no issues. The older ones on the other hand were a bit much at times.

Wkirby was talking about the HF hybrid inverter, the RS, which victron has.

For ESS not available he referenced the RS model, which is quiet and has basic capabilities (no feedin etc).

0 Likes 0 ·
Show more comments
wkirby avatar image wkirby ♦♦ commented ·

1. As nickdb kindly clarified, I was referring to the MultiRS not the MultiPlus II.
2. Again, I was referring to the MultiRS, maybe not even submitted for certification yet.
3. If it were a mere settings change or flick of a DIP switch accessible to the casual user, then yes. However there are (required) barriers in place in the form of a device firmware change requiring the deliberate use, in this case, of dedicated software, a programming dongle and protection by a complex password.

When a MultiPlus is connected to the network in standard mode it is not capable of feed in. It only operates as a charger and also passthrough to loads on AC output, similar to a UPS in a computer room. UPS' or a battery chargers do not require approval because they aren't capable of feed in.

Similarly, standard electric cars don't require any approval either even though a firmware alteration could make them V2G capable at a later time. Only if the car's firmware is altered to make it feed in capable then it would require the approvals. Cars would probably have a different approval standard from G99. I can imagine DNOs welcoming the prospect of evening time battery availability like a terrier would a welcome basin of lean mince.

Remember, there are a multitude of instances where inverter/chargers, like the MultiPlus, are employed in standard mode. Boats, caravans, motorhomes, coaches, emergency service vehicles, welfare buildings, outside broadcast vehicles, food vending outlets, kiosks and so forth, the list could go on. It would be most impractical for installations to require approval to feed in when they can't.

I dare say that there are probably more inverter/chargers around the world operating in standard mode than those operating in grid parallel mode.

0 Likes 0 ·
hominidae avatar image
hominidae answered ·

IMHO fan noise is only an issue if the inverters do not work behind closed doors.

What you defnitely need is some kind of structure-borne sound isolation...You can use anchors/dowels from sanitary installations (rubber mantled dowels) and also place a standard hard rubber pad (like a terrace pad, approx 10-20mm thick) between unit and wall for each mounting hole.

Works wonders....I don't hear a thiing from my 3phase setup with 5000kVA Multipplus-II when in my living room, that sits right above the cellar room where these are mounted and whinning loud.

7 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

johnone avatar image johnone commented ·

Thanks for sound isolation advice (see my comment above for what I'll try). Do you have a link to 'rubber mantled dowels'? Wondered about the supporting capacity of sanitary fixings.


0 Likes 0 ·
hominidae avatar image hominidae johnone commented ·

...see here (only in german, I am afraid): https://www.stabilo-sanitaer.de/schallschutzduebel-16-mm-ohne-bund/a-437146/ ...don't worry about the load these can carry...they are used for heavy washing basins and such. ... you should be able to source these or alike in your local DIY shop or online

0 Likes 0 ·
wkirby avatar image wkirby ♦♦ johnone commented ·

These kind on things?

1667584747886.png

0 Likes 0 ·
1667584747886.png (31.4 KiB)
johnone avatar image johnone wkirby ♦♦ commented ·

The sound insulation dowels @Hominidae mentions look good but I can't find them in the UK (only an Amazon UK seller, who's sold out). Maybe we should join the EU. The anti vibration bobbins also look good - could core drill holes in the wall (brick in my case), and set the bobbins in resin (Everbuild Anchorset, that sort of thing). Is that what you were thinking?


0 Likes 0 ·
wkirby avatar image wkirby ♦♦ johnone commented ·

RS (you can't get more British than that) sell anti vibration mounts too.

https://uk.rs-online.com/web/c/?searchTerm=anti+vibration+mount

0 Likes 0 ·
hominidae avatar image hominidae johnone commented ·
The manufacturer has it's own online Shop and is also to be found on eBay....wonder if they would ship internationally. But I also can't think, that there is no other manufacturer/ source of these. As said, I got mine in a local DIY shop (Germany though).
0 Likes 0 ·
dancrompton avatar image dancrompton johnone commented ·

These might do the trick.

https://rawlplug.co.uk/product/rawlnut-flexi-plug-with-screw/

0 Likes 0 ·
dancrompton avatar image
dancrompton answered ·

In case anyone has missed it. A free retrofit cure for the excessive fan noise.