Hay whats this status mean ?
Works properly but dont know why is ext control status.
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Hay whats this status mean ?
Works properly but dont know why is ext control status.
Are you running the latest OS? I guess no one reads release notes.
https://www.victronenergy.com/blog/2022/09/13/venus-os-v2-90-generator-controls-in-vrm-remote-ve-can-rv-c-venus-os-large-and-more/
a small change, but one that is good for everyone to know: after the upgrade, Multis and Quattros in a DVCC enabled BMS systems now report their state as External-control- instead of Bulk or Absorption. There is no bulk -> absorption -> float charge algorithm when controlled by BMS, and there never has been. This cosmetic adjustment more accurately displays what is actually happening with the battery charge profile when controlled by a BMS. This change will reduce questions like “Why does my system never go to float …is there something wron
@mk1 Your system is operating on 'External Control'.
@mk1 Mine is also on 'Optimised' (W/o BL) but mine has a different text on the same view.
Hi,
I also realized today, that "ext. control" is mentioned.
After reading many posts in this forum, I think I found the answer:
ESS - Multiplus status - VenusOS 2.92
"The status of a multi in an ESS has been external control for quite some time. It is the correct status as it is being controlled externally c/o DVCC."