Multiplus II and Hoymiles Microinverters

The Multiplus II can control the output power of an inverter using the frequency: the higher the frequency the MP2 creates, the lower the output of the inverter. This works well with Fronius inverters.


Question: Does this also work with Hoymiles inverters? HM-1500 for example.

Multiplus-II
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

ojack avatar image ojack commented ·
This would be interesting for me to.

I would like to install the single phase HM-1500 and the three phase HMT-1800-6t at ACout1 on a three Phase System of 3 MP2 3000.


1 Like 1 ·
5 Answers
kai-fuchs avatar image
kai-fuchs answered ·

Are there any updates on this topic?

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

jetlag avatar image
jetlag answered ·

I would say, yes, this should work. This is, as far as I remember, a request of the VDE AR-N-4105 (at least for Germany).

I don't have access to the docuement, but once had the chance to have an insight. It should be this chapter: 5.7.4.3 Verhalten der Erzeugungsanlage am Netz - Wirkleistungsanpassung bei Über- und Unterfrequenz


And additionally, Andy from the Offgrid Garage, has such a combo running with the MP2 and some other "Micro-Inverter" and this works fust fine. Please check his youtube channel.

As the Hoymiles Inverters are all qualified against the german standard, I would say this should work.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

ojack avatar image
ojack answered ·

Yes it works with my Hoymiles HM-1500 and HMT-2250-6T.

And it should work with every inverter which fulfills the regulations of grid coupled operation.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

alexander-uhde avatar image
alexander-uhde answered ·

This does also work well with APSystems microinverters on my site.


But you should be aware that frequency shifting will only Work off-grid.

If the MP2 ist connected to the grid via Ac-in IT cannot shift the frequency on Ac-out.

Regards

Alex

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

jetlag avatar image
jetlag answered ·

And the corresponding assistant in the MP2 must bei implemented.