I have Multiplus-II 2x120V that was just installed in a fifth wheel RV (together with Smart Lithium batteries, Lynx BMS, Cerbo GX and GX Touch 50). The Multiplus is connected behind an EMS and a Generator transfer switch.
I have it currently connected to 20 amp 120V single phase shore power US GFCI outlet. In Cerbo GX I limited the current to 10 amp just to be on the safe side.
The problem is the Multiplus trips the GFCI outlet. This has never happened before I installed the Multiplus-II in my RV.
To diagnose it I connected it to a different (non GFCI) outlet in which I wired a current meter on the ground line. I also turned off the main 2 pole 50Amp breaker on the RV breaker panel (that is connected to AC out 1 of the Multiplus).
When I turn on the power to the shore outlet with the current meter wired on the ground wire:
0) I turned the Multiplus off using the GX Touch interface
1) First my EMS has a delay of 144 seconds before turning on the power. During that time the current on the ground wire measured at the outlet described before is ~0.5 mA. So far so good.
2) After the 144 seconds delay the power to Multiplus turns on. The current on the ground wire is 1.5mA. So far so good.
3) If using GX Touch I switch Multiplus to Charger mode the current on the ground wire jumps above 10mA, which is way above the level that trips the GFCI (4-6mA).
Then to rule out a faulty cable connected to AC out 1 I disconnected a ground wire from the Multiplus AC out 1 and on the other end of that cable I disconnected a ground wire from the RV service panel, so there is no way that the cable connected there is introducing any current on the AC in ground wire. Still all the measurements were exactly the same.
For what is worth the current seems to decrease over time (when the charing current decreases), but even with completely full batteries it is ~5.5mA.
Also: the 120V cables are Romex 6 AWG, the ground is a single solid conductor so there is no risk of one of the strands not getting into slot.
I have also verified with a thermal camera that no wire connection to AC in/out is overheating.