Does anyone have this working ?
A have a raspberry venus os 2.90-10 , 2 x mppt controller and now 2 smart stunt , one as a battery monitor and the other a dc load monitor connected to my inverter .
Like :- DVCC not compensating for inverter - Victron Community (victronenergy.com)
it will not compensate for the extra load , I've deleted the smart networking from each device , tried rebooting , checking every setting .
If 20 amp are coming from the controllers with a 10 amp load and I set the limit to 15 amps it sets the controller's 15 amps not the maximum going into the battery which is now 5 amps .
CAN I FIX IT WITH NODE-RED
Can I read the load and just set the dvcc limit to 15 amp + load every 5 seconds ? or would the charges be saves somewhere and saved to flash ?
THAT IDEA WORKS
I've tried that idea and it works to within 1 amp , so if I set a maximum of 10 amp the charge is 9.0 to 11 amps , better now it will raise with the load.