Hi guys..
I have my off-grid system up and running without a glitch since July 1st.
Today, suddenly it shut down. At that time probably the load was large, but did not get any overload notification. Something smell burned, but could not identify the location, not sure it was from the area the off grid equipment is placed or elsewhere. All devices seem functional.
I played with turning on of devices etc.
Eventually, I realized it shuts down when a "big" load starts. But thing is, all these loads where served perfectly so far.
So when I have a load of ~ up to 800w no problem. when I go over 1.5kw for sure it shuts down.
No errors reported.
I tried to identify which device is causing, but did not. The only thing I identified is the following:
When using an amp clamp I measured the master having increased A drawn when increasing loads while the slave was starting from 0.3A and never went over 0.5A.
When connecting to each device with MK cable, both inverters where identified and seem fine in the app.
About the setup:
2 Multiplus Compact 24v/2000 in parallel. Both AC/DC cables are of equal length to <2mm (what I can measure)
505A 2v lead acid , fully charged when happend.
Bluesolar 150V/70A with 6 panels, 2.670w in parallel/series
Any hints would be helpful..starting with what causes shut off with out error that requires the button to be set to off and on.