This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Did you try Unit ID 100?
Hello! I have to pick up the topic again, with UNIT-ID 100 I can not read the register 2901. Who can help me? I would like to specify the minimum discharge value SOC via Modbus. Thank you!
I assume you have ESS enabled in your system since register 2901 refers to "ESS Minimum SoC (unless grid fails)"
Are you getting an error when you try to retrieve the value from Unit ID 100 or does it just return 0?
Not sure which device the dbus-service-name "com.victronenergy.settings" is referencing if it does not exist for ID 100. Victron can probably answer.
@Guy Stewart (Victron Energy Staff)
Pat
You need to download the Modbus TCP Registry spreadsheet. In can be found here:
https://www.victronenergy.com/support-and-downloads/whitepapers
It also has a Unit ID to Device ID sheet.
Pat
8 People are following this question.