Hello! Who can help me with a Modbus TCP connection to the CCGX? Under which unit ID can the address 2901 be read or written?

Modbus TCP
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
wkirby avatar image
wkirby answered ·

Did you try Unit ID 100?

6 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

rolandp avatar image rolandp commented ·

Hello! I have to pick up the topic again, with UNIT-ID 100 I can not read the register 2901. Who can help me? I would like to specify the minimum discharge value SOC via Modbus. Thank you!

0 Likes 0 ·
Show more comments
rolandp avatar image rolandp commented ·

Or in other words, how can I specify the SOC value via Modbus TCP to the CCGX? How do I have to address?

0 Likes 0 ·
Pat Davitt avatar image
Pat Davitt answered ·

You need to download the Modbus TCP Registry spreadsheet. In can be found here:

https://www.victronenergy.com/support-and-downloads/whitepapers

It also has a Unit ID to Device ID sheet.

Pat

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

rolandp avatar image
rolandp answered ·
Hello! The Modbus function to write register 2901 works, thanks for the support. I have another question: where can you read what the current utilization of the solarcharger is? Is the Maximlae Powerpoint visible in a Modbus register? I want to find out how much power reserve my solar panel still has to control a heating cartridge. Best regards, Roland