Anti islanding - multiplus ii vs easysolar

Need to decide between multiplus ii based system and easysolar system. Can anybody state the difference in terms of hardware, configuration , functionality, cost or any other considerations to take note of before selection.

Multiplus-II
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
JohnC avatar image
JohnC answered ·
3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Rob Duthie avatar image Rob Duthie commented ·

Hi John

So the new Easy Solar GX2 has anti islanding system in it like the mulitplus 2 units?

So they can be connected to the grid if they are approved, are you getting approvals for NZ?

Regards

Rob D

NZ

0 Likes 0 ·
Show more comments
nigelfxs avatar image
nigelfxs answered ·

Hi Karel, some some countries/cities have a published list of "approved" inverters that are allowed to be connected to the Mains grid. This is due to the safety requirements of the anti-islanding system.

For example, the Easysolar is not allowed for a Grid-Tied installation in South Africa (according to NRS 097-2-1), but the Multigrid, Multigrid-II and Multiplus-II units are allowed.