Hello
I have three phase multiplus 2 setup, and solar edge 16 SE photovoltaic inverter, is it possible to shov production of my solar in vrm online portal, the setup for photovoltaic inverter finds nothing.
thank you
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Thank you I went for first option, but there is something wrong and I cannot figure out what, look at this readings..
When the pv was 11kW the grid showed -15 kW and battery charging 4.7 kW ??
What is used to measure the grid?
Also, what is your current question?
Originally you posted this question.
I have three phase multiplus 2 setup, and solar edge 16 SE photovoltaic inverter, is it possible to shov production of my solar in vrm online portal, the setup for photovoltaic inverter finds nothing.
if you look at the details, the inverters are still working as they should , the big number is wrong
and I cannot figure out why.
Internal CT is not very accurate and sometime they don't work.
it is better to use power meter like ET340 or EM24.
look at the picture I posted, the grid square, the internal ct in inverters are showing -69,-65 and 191 now how that add's up to 898W ??
the internal ct are fine, I dont know how the big number 898W is calculated.???
hear you and thank you for your time but please explain me how could be the internal CTs fault , from the details on the grid square you can see the CTs are showing correct value, the CTs are ok.
There is some math going on here, somethink is added to the grid when the pv inverter was introduced to the system. If I brake lan connection to the solaredge inverter the grid consumption is in sinc with the solar edge externa import/export meter.
Something must be configured wrong.
40 People are following this question.