question

pirpy avatar image
pirpy asked

solar edge pv inverter on vrm online portal

Hello

I have three phase multiplus 2 setup, and solar edge 16 SE photovoltaic inverter, is it possible to shov production of my solar in vrm online portal, the setup for photovoltaic inverter finds nothing.

thank you

VRM
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
marekp avatar image
marekp answered ·

@pirpy

https://www.victronenergy.com/live/venus-os:gx_solaredge

You can also install Power Meter ET340 at the output of your SE and connect it to your GX device.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

pirpy avatar image
pirpy answered ·

Thank you I went for first option, but there is something wrong and I cannot figure out what, look at this readings..kaj-je-narobe.jpg


kaj-je-narobe.jpg (146.6 KiB)
11 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

marekp avatar image marekp commented ·
@pirpy

I do not understand.

You can see your PV inverter on the dashboard and it is producing 955W

0 Likes 0 ·
pirpy avatar image pirpy marekp commented ·
The number -898 on the grid is wrong, you see the details. on the grid, if you add the phases it is 56 W as it should be.

When the pv was 11kW the grid showed -15 kW and battery charging 4.7 kW ??

0 Likes 0 ·
Show more comments
pirpy avatar image
pirpy answered ·

I want a second opinion

wrong.jpg


the CT's are OK


wrong.jpg (140.8 KiB)
2 |3000