Multiplus Bulk Over Voltage - Cause resolved due to discovery of Multiplus feature

I have a Multiplus 12/1600/70-16 and recently I put it on mains charge as weather has not been good enough for solar charge and VRM is showing it pushing up to 16v in to a bank of two AGM batteries. I can't see any reason for this, any help would be appreciated. I don't know if this is temperature compensation error and now batteries have been damaged

Multiplus Config

1663166877776.png


VRM

vrmerror1.png

MultiPlus Quattro Inverter Charger
1663166877776.png (26.4 KiB)
vrmerror1.png (49.1 KiB)
4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

klim8skeptic avatar image klim8skeptic ♦ commented ·
Multiplus charge current of 0amp.

What is driving the battery voltage up??

0 Likes 0 ·
Show more comments
southsideph avatar image southsideph commented ·

This was an earlier screenshot


1663243558381.png

0 Likes 0 ·
1663243558381.png (52.3 KiB)
Show more comments
2 Answers
southsideph avatar image
southsideph answered ·

It Looks like the mystery of the over voltage has been resolved. The story so far is the Multiplus kept overvoltage charging, voltage was increasing to 16V+ volts on a 12V system.

The only reference I had was 16.2V is the standard equalisation voltage. Equalisation was disabled so I thought. there was no indication even VRM does not report the Multiplus as being in equalisation mode.

Further research identified there is a feature in the Multiplus, in that if you switch between On and Charge only without going to the off position first, this puts the Multiplus into automatic equalisation or forced absorption irrespective of any other settings- don't really understand this but seems this is the case.

Enter the Digital Multi Control (DMC) - This was fitted to enable switching between modes and adjusting the AC input current Grid/Shore/Generator. The other reason for the DMC was to be able to disable the inverter etc. when not required.

So because of the above feature, it seems i set the Multiplus into automatic equalisation by switching the DMC from ON to Charge Only, the only way to identify is an obscure flashing of a combination of LEDs.

Unfortunately this lesson has come at high price and voltage sensitive equipment

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

marc-heide avatar image
marc-heide answered ·

do u have other equipement installed? maybe third party solar converter or something like that.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

southsideph avatar image southsideph commented ·
It is a complete Victron installation - Orion, 2 x 100/20 mppt, BMV712, Battery protect connected via PI running GX OS 2.89.