Just curious why the MPII 10KVA (and 8KVA) cannot be used in Parallel?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Just curious why the MPII 10KVA (and 8KVA) cannot be used in Parallel?
The current hardware for the MP II and Quattro II up to 5kVa does allow paralleling, the 8k/10k/15k hardware doesn't -- Victron haven't said why, but have said this can't be fixed in software so a new version of the hardware will be needed to allow this.
This is presumably why the Quattro II bigger than 5kVA haven't been released yet, paralleling is seen as an essential feature for Quattros (less so for the Multiplus) -- which is annoying because I will need a Quattro 48/10000 soon and would much prefer if it was a Quattro II, but there is no release date for this yet... :-(
Parallel is still not possible with the 15kVA MP-II.
It is on the 2nd page.
Paralleling is not supported for these models (revision from previous post).
We can have a max. of 3 units in 3 phase configuration only - should be applicable to 8/10/15kVA units - provided the units have the same hardware.
We have a 3 phase installation with 3x MultiplusII 10kVA that has been running smoothly for more than 8 months now.
64 People are following this question.