Voltage problem between neutral and earth in battery operation.

Hello,


I have an old Phoenix multi 24V/ 1300W that still works. I have a problem with the neutral which generates current. I connected the phoenix to ground as well as the mppt. The phoenix is plugged into an isolated site without a generator or edf....


Should I touch J33 or something else...?


20220823-151902.jpg

20220823-134525.jpg


thank you very much.


Fabrice

Grounding
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

lifeingalicia avatar image lifeingalicia commented ·
blue wire on PE (earth) ?
0 Likes 0 ·
1 Answer
fabrice avatar image
fabrice answered ·

No, I plugged in a ground but I only had this cable left.


I have current in the neutral at the 80v output. Do I need to install a neutral contactor or change a Phoenix setting?


thank you

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

netrange avatar image netrange commented ·

How did you measure the voltage? Against PE?

You can only measure a current if it can flow over a load.

0 Likes 0 ·