Question on Comms for Victron Multiplus 12/3000/120

About to purchase a Victron Multiplus 12/3000/120 Inverter/Charger and the MultiPlus Digital Multicontrol Panel.

Can I connect the Inverter to both the Control Panel RJ45 and RPI GX via MK3 RJ45 at the same time? Is there anything to be aware of?

TIA

VE.Bus
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
boekel avatar image
boekel answered ·

Yes, only thing is when a digital control panel is connected, you cannot turn on/off the inverter (or change AC-in current) with the Venus device.

4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Todd Wackford avatar image Todd Wackford commented ·

So I can't send command on/off, or current limits via MODBUS-TCP input registers? Or, I cannot modify via Venus device user interface?

0 Likes 0 ·
boekel avatar image boekel ♦ Todd Wackford commented ·

That is correct.
If you're smart with the software side, you might want to make your own control panel :)

https://community.victronenergy.com/articles/12400/service-to-turn-multiplus-onoff-via-digital-input.html

0 Likes 0 ·
Todd Wackford avatar image Todd Wackford boekel ♦ commented ·

After reading the article referenced, I think I may have worded my original question incorrectly.

I want to be able to turn off the charger side of the multi via modbus-tcp register input/command if it connected to the control panel. Is that possible?


0 Likes 0 ·