Question on Comms for Victron Multiplus 12/3000/120

About to purchase a Victron Multiplus 12/3000/120 Inverter/Charger and the MultiPlus Digital Multicontrol Panel.

Can I connect the Inverter to both the Control Panel RJ45 and RPI GX via MK3 RJ45 at the same time? Is there anything to be aware of?

TIA

VE.Bus
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
boekel avatar image
boekel answered ·

Yes, only thing is when a digital control panel is connected, you cannot turn on/off the inverter (or change AC-in current) with the Venus device.

4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Todd Wackford avatar image Todd Wackford commented ·

So I can't send command on/off, or current limits via MODBUS-TCP input registers? Or, I cannot modify via Venus device user interface?