question

damon-blumenstein avatar image
damon-blumenstein asked

Current limit at 15 but only using 10?

Anyone know why when I set the limit to 15amp, the Multiplus is only allowing 10-11amps and pulling the rest from battery? I tried 20amp but then the generator gets killed by the spike when AC kicks on. screenshot-20220805-214519-vrm.jpg

powerassistinput current
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
kevgermany avatar image
kevgermany answered ·

Is there a limit on the grid hookup?

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

damon-blumenstein avatar image damon-blumenstein commented ·
Yes, it's at to 15, that's the problem, it's only pulling 10-11. Once the air condition turns off and the load isn't so high, it charges the battery with around 14 amps. Once the AC load is back, it drops back to 10-11A and pulls the rest from the battery.
0 Likes 0 ·
Show more comments
Alexandra avatar image
Alexandra answered ·
@Damon Blumenstein

If you have weak ac enabled it will do that.

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

damon-blumenstein avatar image damon-blumenstein commented ·

Week AC is not enabled. 1660530128419.png


Does dynamic current limit cause this? I assumed I should have it checked to help the generator from getting full bursts of current draw.

1660530296932.png

0 Likes 0 ·
1660530128419.png (11.3 KiB)
1660530296932.png (6.3 KiB)
Alexandra avatar image Alexandra ♦ damon-blumenstein commented ·
@Damo n Blumenstein

It is possible that is could be the cause, usually it only affects short term current draw from the generator.

But your battery charging amps are set at 120A, on a 12v system that is 1440W of charging at 12v so if you don't have other loads on this will be all the system draws.

0 Likes 0 ·
Alexandra avatar image
Alexandra answered ·

@Damon Blumenstein

Try switching off power assist, or changing the boost factor.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

damon-blumenstein avatar image damon-blumenstein commented ·
I'll try that, what power factor do you suggest? My generator is a small 3000 watt that I would call 2500 in reality.
0 Likes 0 ·

Related Resources

Additional resources still need to be added for this topic