Advise load output MPPT 75/10. On which pins should I place the jumper if I want to charge a 48ah LiFePO4 battery with a 36Watt solarpanel (see image)?

zp.jpg

MPPT Controllers
zp.jpg (28.3 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
ej-beekeeper avatar image
ej-beekeeper answered ·

Ah, I found the answer. if I don't use the Load terminals the jumper can be removed.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

kevgermany avatar image kevgermany ♦♦ commented ·
You posted while I was typing. I'd still connect to load, not the battery.
0 Likes 0 ·
kevgermany avatar image
kevgermany answered ·

With lithium it's very important not to discharge too far. Usually the BMS will prevent excessive discharge.

Leaving the jumper off is for lead acid.

You haven't given us the battery specifications, but jumper between 1 and 2 gives a cut off voltage of 11.1V, while bridging 2 and 3 gives a cut off of 11.8V. Check the battery specs, if in doubt bridge 2 and 3.

I take it you're able to use Victron connect to configure for LiFePo4 batteries.