question

mikeb avatar image
mikeb asked

Mppt error inf67

Any one ever had this error ?


Ve direct to colour gx

Byd bms

All been working fine for over 4 months then this error message nothing in the Manual for inf67

To other moots working ok with byd bms


All firmware up to date

Regards

Mike

error
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
JohnC avatar image
JohnC answered ·

https://www.victronenergy.com/live/mppt-error-codes

Err 67 - BMS Connection lost

The charger is configured to be controlled by a BMS, but it does not receive any control messages from a BMS. The charger stopped charging, as a safety precaution.

Check the connection between the charger and the BMS.

How to reset the charger, to de-couple it from the BMS

When the charger needs to operate in stand-alone mode again, not controlled by a BMS, it needs to be reset:

  • VE.Can solar chargers, go into the setup menu, and change setting ‘BMS’ from ‘Y’ to ‘N’ (setup item 31).

  • VE.Direct solar chargers, reset the charger to factory defaults with VictronConnect, and then reconfigure it.

Note that (solar-)chargers automatically configure themselves to be BMS-controlled when they are connected to one; either direct or via a Color Control GX or Venus GX.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

mikeb avatar image
mikeb answered ·

It’s not err 67 tho


Is inf 67


Have seen error 67 when it was tested as per the configuration of the byd and mppt

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

mikeb avatar image
mikeb answered ·

Has anyone seen the error message before ?


Has been running fine on a system form4 months with no issues


Know a err 67 is a connection lost error message


Unplugging the ve direct to usb and substituting to for a known working cable doesn’t solve the issue


But must admit haven’t tried powering the unit down and resetting it from default again


Just a question if any one has seen or had the error before and what solved it



2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

sean avatar image sean commented ·

Mine do that when they cant see the BMS (not a BYD system), which seems to echo other answers. A selective reboot and checking of data cable security might resolve your issue.

0 Likes 0 ·
mikeb avatar image mikeb sean commented ·

Thanks for the reply


Have to other mppts running they have not been affected


Have more of a idea when I bust the installation over the weekend

0 Likes 0 ·