Multiplus different AC In and AC Out

Hi All

I wondered if anyone can give me some advice on how to resolve this matter...

Setup: MP2 5KVA, MPPT, 12KWh Lifepo4,CerboGX, not grid tied, Main AC In from grid to charge batteries.

Issue: I turned off the MP during a charging cycle since I did not need the batteries to be full (it was sunny the day after). Went to charge batteries again a few days later but, was not able to do it. Solar/MPPT is able to charge the batteries - no problems here. Inverter working as well - no probs.

As you can see from the photo blow - the AC In is at different voltage to the AC Out.

Tried: 1) Switching AC and main rocker switch and also breakers on/off - nothing. 2) Did a reset in Remote Console - nothing. 3) Selected "Weak AC In" in V Config

I have read that I may need to change the country grid in configuration in VE Config and have a range of AC In / Out so that the MP can latch on? VE Config needs a password - so I will be trying this next.

Any advice on the above issue/s will be much appreciated.

1653671774946.png

Multiplus-II
1653671774946.png (11.8 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Alexandra avatar image
Alexandra answered ·

@TrungT

Its state is inverting, therefore it is not connected and synchronised to grid (even though it is present)

There can be several reasons, since it accepted grid before, you can leave the grid code. Check your inverter in the gx is not set to inverter only.

screenshot-20220527-192551.jpg


2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Trung avatar image Trung commented ·

Hi Alexander

Many thanks for your prompt response - yes, that is the only things I can think of doing - other than that I am snookered or stuck. It was working great without any problems for 13-14 months.!!

I think you are correct and there is Loss of Mains (LOM) detection....

If I Disable it for the country that I am in, are there any precautions I need to take before or after doing so??

Many thanks


0 Likes 0 ·
Show more comments
Trung avatar image
Trung answered ·

Hi Alexander

I am not using ESS assistant and have not tried AC Ignore System. I use a wifi switch/plug for greater flexibility.

I only have AC In and I am not grid tied on AC Out - that goes to a secondary ring in my house.

I shall have look at trying out Type B in the country grid code and see if the MP latches onto the AC Input. (I shall have a look for the UK).

In terms of disabling LOM - I thought this is an often done thing especially if you have a poor AC Input that can vary to AC Output such as generators.

I have checks the connection and feed into the MP - and, it is OK.

Ok...a bit of experimentation for me tomorrow then.

Many thanks again for your advice...