My MultiPlus-II 48/5000/70-50 GX is combined with 1 Pylontech US2000C (test setup) and a CT is configured as a grid tied ESS system (AC IN connected only). The Multiplus II GX detected the batteries correctly. The Discharge Current Limit (Pylontech battery -> Parameters) is 25Amps. ESS assistant is installed of course and firmware is up to date.
When a largish load engages, such as the water heater, the Pylontech battery starts discharging at well over 25Amps (50Amps or greater sometimes) which then causes the red led on the battery to start flashing! Why does the system not keep the discharge to 25Amps?
I have tried to Limit Inverter Power and set the Maximum inverter power to 1000W using the ESS functionality for example (see below), but this does not seem to be effective either.
I know that in theory the MultiPlus-II 48/5000/70-50 GX requires more battery capacity to provide the power requirements from heavier loads which is the aim eventually (when more batteries are obtainable), but I assumed that the functionality of the Discharge Current Limit or Limit Inverter Power would allow this set up to work without overloading the single battery currently in use?
Current set up:
Overcurrent in action:
DCL:
Limit Inverter Power: