DVCC is a GX device setting. It cannot be set on a RS Inverter directly.
It is not really needed as there is only one charge source and the mppt is 80amps. So on a correctly sized battery bank you would never be able to over amp during charging in anycase.
If you have more mppts in the system, then it is advisable to use a GX.
Hi, thanks for your answer. In fact I have one more device (MPPT 150/35) and a CerboGX. On the CerboGX , I have activated DVCC and limited the total charge current to match the batteries. I left all other options off. What I am not sure is, if the DVCC setting on the CerboGX is honoured by the RS Inverter.
80A and 35A of charging shiuld still be within the bank capabilities. And with the correct voltages programmed will charge correctly.
Especially if the batteries are communicating with the system.