question

PeterM avatar image
PeterM asked

Multiplus and Multiplus 2 compatibility

Can you parallel up similar size Multiplus and Multiplus 2 devices - single phase ?

Multiplus-II
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Paul B avatar image
Paul B answered ·

No only a multipus to a multiplus

or a multiplus II to a Multiplus II

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Guy Stewart (Victron Community Manager) avatar image
Guy Stewart (Victron Community Manager) answered ·

Hi Merle,

All units in a parallel or 3 phase system must be the same type and firmware version, this includes same size, system voltage, and feature set.

The type is indicated by the first four digits of the firmware version number. For details, see the “VE.Bus Firmware Numbering System” section in the VE.Bus Firmware versions explained document.

You cannot parallel a Multiplus with a Multiplus-II. Please read this manual for further conditions:

https://www.victronenergy.com/live/ve.bus:manual_parallel_and_three_phase_systems

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

PeterM avatar image PeterM commented ·

Might be the same answer but not looking at 3 phase though but doubling up capacity

0 Likes 0 ·
Show more comments