question

matt1309 avatar image
matt1309 asked

Energy meter AC loads - PV = grid

Hi,

I have two energy meters ET112's. Grid, PV array and loads both on AC in.

If the meter on loads is set to grid meter (wrong for mysetup) the ac loads is calculated as follow grid + PV = AC loads.

However it doesn't work if energy meter is set to AC loads ie AC loads - PV doesn't equal grid in VRM.

Is there a way to do this?

Thanks,

Matt.



Energy MeterAC PV Couplingac coupling
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
shaneyake avatar image
shaneyake answered ·

Your setup should be

Grid -> Grid Meter -|

| - PV meter -> PV inverter

| - Non Critical Loads
| - Victron Inverter AC input -> Critical Loads

This way you will get 4 blocks on VRM: GRID, PV, AC Loads and Critical Load

screen-shot-2022-05-07-at-53625-pm.png


4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

matt1309 avatar image matt1309 commented ·

Is there a way to get AC loads as the ennergy meter number instead of grid?

Grid -> energy meter 1 -> PV (shed)

Grid -> energy meter 2 -> house with energy meter

I was hoping to use meter on house and meter on PV and then calculate the grid number.

ie grid = house - PV.

It works the other way around is House (ac loads) = grid + PV but venus os doesnt seem to support the other way around


It's not easy for me to add meter before the split of the feeds to shed and house. Hence this situation

0 Likes 0 ·
shaneyake avatar image shaneyake matt1309 commented ·
The simple answer is no, Victron system does not allow this type of install.


Complicated answer is yes, you can do this but you will need a custom script on the GX to do the calculation and act as a virtual grid meter.

0 Likes 0 ·
Show more comments