question

botessj avatar image
botessj asked

Multiplus II 5kVA 48V random output voltage dips

I fairly recently installed a Multiplus II 5kVa 48 system (including Venus GX), connected to 2 x Hubble AM-2 5.5kHw lithium batteries. System runs as purely backup system for load shedding purposes.

This issue that has arisen is that the inverter randomly cuts the output voltage to the loads for a couple of second.

The latest instance happened after a blackout (load shedding). The system took

over and returned seamlessly, and roughly a hour after, the output voltage dipped for a couple of seconds.


-Inverter and GX has latest firmware installed

-System is not overloaded

-AES is not enabled

-Battery bank is CAN bus connected to the GX, via its own logging device (Cloudlink\Riot)

I have checked settings multiple times, and compared to other installations.


Has anybody had similar problem, or have advice as to remedy?

Thanks


voltage-in-and-out.jpg

Multiplus-IIbatteryvoltage
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

6 Answers
botessj avatar image
botessj answered ·

As a sidenote. This does not only happen after loadshedding

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

marekp avatar image
marekp answered ·

@botessj@gmail.com

I do not have the answer for your question but I had similar occurrence but my system showed an error #1 device switched of.

problem.jpg


problem.jpg (175.7 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

nickdb avatar image
nickdb answered ·

There was another member here a while back with hubble issues.

They have not been tested with Victron and are not on the compatibility list.

From that post (you can search for it), it sounds like they can't provide proper settings for victron and may have BMS issues.

Suggest you contact them for support.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Munnik avatar image
Munnik answered ·

I have the exact same problem on 2 x Multiplus 2 sites. One site 8kw BSL other site 5 kw Revov R 100. I have tried multiple settings and cable/terminal checks. The one client is very frustrating and does not understand. I am at the point to remove the system and give him a full refund. I sold Victron to him as one of the best inverters on the market, but because off al the dipping when loadshedding kicks in he does not agree with me. I also find this problem extremely irritating because it is taking up alot of my time. I have installed multiple inferior cheaper brand inverters and have no dipping issues at all. I have searched, Google and spoken to other Victron installers about this, but cant get a answer that works. Hopefully someone on the forum can help me.


Thanks Munnik

7 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Andrew Poluta avatar image
Andrew Poluta answered ·

Hi Guys


I'm having similar issues with the Multiplus II 5 and 8kVA models with the following batteries:

1. Freedom Won E Tower

2. BSL 7 and 8.8kWh

3. Hubble AM2


Many systems have run great for months but just recently started acting up.


If you are based in South Africa please contact me on 082 411 4060, we need to gather as much info as possible.

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

alan-2 avatar image
alan-2 answered ·

Hallo


I have / had the same issue.

To me it looked like the charger section was the problem, so I went out an got external chargers and keep Multiplus in inverter mode…

Also, the offices were using nonAVR generators that went as high as 62 Hz at times…

So now there is no dipping, as there is not changeover and no comms between inverter and charger…

One thing interesting I saw is that Revov has popped up as a battery charging profile on the chargers…

Which means there is a very specific management of these batteries.

Incidentally, we have had two of the 200Ah units with a bad cell, out the box.


It only shows up when you take it off charge.

Then run the BMS software to show individual cells.

You will see on of the cells on 0.0v…


My take- it’s a new venture with teething issues.

It’s a nice concept, getting full use of cells… but…

2 |3000