question

philippe-gonin avatar image
philippe-gonin asked

multiplus 1600VA green inverter led is off

hello i have bought a Multiplus 1600 VA and the leds are always off

there is a correct entry voltage but no AC voltage and no green led on

the fuse seems to be ok

led
9 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

klim8skeptic avatar image klim8skeptic ♦ commented ·
Do you have a battery connected to the multi?
0 Likes 0 ·
philippe-gonin avatar image philippe-gonin klim8skeptic ♦ commented ·

yes of course 2 12V batteries and a victron mmpt with float led on

0 Likes 0 ·
klim8skeptic avatar image klim8skeptic ♦ philippe-gonin commented ·
HMmmm.

If the multi has 12 (24?)v at its input terminals, and is switched on, it should work / green led.

Disconnect any thing plugged into the VE bus ports.

0 Likes 0 ·
Show more comments
1 Answer
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

Is the MultiPlus switched to ON, not charger-only?

5 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

philippe-gonin avatar image philippe-gonin commented ·

yes of course

0 Likes 0 ·
Matthias Lange - DE avatar image Matthias Lange - DE ♦ philippe-gonin commented ·
Is the wire bridge in the remote connection? Any remote panels connected? Anything else that could control the MultiPlus?

DC voltage is at the battery terminals of the MultiPlus?

0 Likes 0 ·
philippe-gonin avatar image philippe-gonin philippe-gonin commented ·
yes the wire bridge is present

leds are off with or without panels

the victronconnect app and voltmeter mesure show 27.4 V at the DC entry of the Multiplus


0 Likes 0 ·
Matthias Lange - DE avatar image Matthias Lange - DE ♦ philippe-gonin commented ·
VictronConnect app? So you have a VE.Bus Smart Dongle?

Is the Multi switched to ON in the app?

What other components do you have?

0 Likes 0 ·
philippe-gonin avatar image philippe-gonin Matthias Lange - DE ♦ commented ·
VICTRONconnect app is for the mppt but we can see voltage batteries on it

i don't have VE bus smart dongle

i have no voltage in the inside fuse when switch is on, does it mean tht fuse is KO even if it seem clean ?

0 Likes 0 ·

Related Resources

Additional resources still need to be added for this topic