Multiplus Compact 24/2000 Charging Tesla Model S Battery

Greetings

I have putting together my setup and recently received my Multiplus Compact, what a nice unit! After inital configuration i discovered that in the charger settings aren't conducive to Tesla LiIon batteries.

Question 1: Does anyone have this battery, what settings do you set in the charger tab?

Question 2: I have AC In connected, is there a way to prioritize solar over AC In?

Thank you

battery charging
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
boekel avatar image
boekel answered ·

I'd use:


-charge voltage (in old terms: absorbtion) 6x 4.1 V = 24.6 V

-float I usually set a little bit lower to prevent trickle charging: 24.6V (or 24.5) [edit, this was first a typo, adjusted)

-discharge voltage: 6x 3.3V = 19.8V


Pleas note: a battery protect only works in one direction, and is not adviced to use between battery and inverter.
What BMS are you going to use?

I'm not using a Tesla module myself at the moment, but other 6s battery modules with Tesla BMS slaves (plus SimpBMS)

12 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

aserio avatar image aserio commented ·

Thanks Boekel.

I will use those settings.

So i should remove the battery protect from in between the battery and inverter? Where should i place in the diagram?

As far as BMS, I am still waiting for the Batrium WatchmonPlus which they promise it will manage these cells. I have also looked at Tom's simpBMS, i've asked him, via PM, if he has any in stock. I am not sure however if my slave (see below) will work.


0 Likes 0 ·
tesla-slave-bms.jpg (137.8 KiB)
sean avatar image sean aserio commented ·
0 Likes 0 ·
Show more comments
Show more comments
geomz avatar image geomz commented ·

Please note that 25.6 is way too high for these modules. 25.2 is the max they should be charged at, and even that should be avoided. Is that a typo or am missing something? :)

I personally would not charge those modules above 80% capacity of around 23.8, (they will last longer and gives one a wider margin of error in case of mishaps) but 24.6 should be perfectly fine for near-full capacity.

0 Likes 0 ·
boekel avatar image boekel ♦ geomz commented ·

Thank you!!! that was a typo (on the 'float' charge voltage)

I've edited the post.

I agree: lower voltage = more life.

When using for storing solar the charged voltage isn't kept long, so then I have less problems with it. (on backup system's I also use a lower voltage)

0 Likes 0 ·