My understanding is the Quattro can output 5000 KVA in total, is that split between each leg? Does that mean each leg is limited to 2.5kva split evenly? or can it be unbalanced?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
My understanding is the Quattro can output 5000 KVA in total, is that split between each leg? Does that mean each leg is limited to 2.5kva split evenly? or can it be unbalanced?
It is 5kva total (4000W). Depending on application.
For example on a backup system, loads you don't want to ever switch off are on AC1. (lights wifi, fridge) so not high loads but critical.
Non essential loads on AC2. These can then be programmed to auto powercut in the case of low SOC to prioritise critical loads. Or programmed to load shed if a person accidentally switches on too many big draw items. In its default programming AC2 is off when there is no grid connection.
Ok, it was my understanding the Quattro is Split phase, and does AC1 and AC2 all the time , it seems like that might be configurable then?
Victron only has single phase devices.
If you need split-phase you need two units and configure them to work together as a split-phase system.
If split phase is what you are looking for then you need the multi II 2x120.
Or you can configure two units in split phase but make sure you get the right models.