5k Quattro Max Inverting Output per leg

My understanding is the Quattro can output 5000 KVA in total, is that split between each leg? Does that mean each leg is limited to 2.5kva split evenly? or can it be unbalanced?

MultiPlus Quattro Inverter Charger
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Alexandra avatar image
Alexandra answered ·

@neoneddy

It is 5kva total (4000W). Depending on application.

For example on a backup system, loads you don't want to ever switch off are on AC1. (lights wifi, fridge) so not high loads but critical.

Non essential loads on AC2. These can then be programmed to auto powercut in the case of low SOC to prioritise critical loads. Or programmed to load shed if a person accidentally switches on too many big draw items. In its default programming AC2 is off when there is no grid connection.

5 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

neoneddy avatar image neoneddy commented ·

Ok, it was my understanding the Quattro is Split phase, and does AC1 and AC2 all the time , it seems like that might be configurable then?