mvader (Victron Energy) avatar image
mvader (Victron Energy) asked

Venus OS v2.83 released officially

Hi all,

just a short announce: v2.83 has been released officially. Thank you for the testing and feedback.

Changes are on Victron Professional; no changes and exactly the same as also announced here: https://community.victronenergy.com/questions/120577/venus-os-v2831-available-for-testing.html..


With v2.83 out, all issues that we are familiar with that started with the (big) v2.80 release are now solved.


All the best, Matthijs

Venus OS
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
n-dee avatar image
n-dee answered ·

Big problems here with 2.83 and 2.84

Grid Setpoint isn't met anymore.
In my setting (Grid setpoint -20, total of all phases) it is at approx -180 all the time (selling to grid)
upon switching to individual phase, it goes to approx +180 (buying from grid)

Even setting it to +80 doesn't change this when on total of all phases.
please @mvader (Victron Energy) could anyone look at this. Feel free to try and adjust.

ID 58337

Problem started tonight - maybe with auto update to 2.84 (?)
Got back to 2.83 but problem still here.

After a reboot its ok some minutes but then it gets to -180 again.

System: 6x MP II 5000, 5x MPPT, 1x Fronius Symo, 45kwh BYD LVL - all firmwares on latest.
Unfortunately can't go back to 2.73 (which was fine) as i already was on 2.84

1645399150381.png



1645399150381.png (31.3 KiB)
6 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

pau1phi11ips avatar image pau1phi11ips commented ·
@N-DEE That's a beast of a system!

Grid Set point working fine here on 2.84 but just on a single MP II

0 Likes 0 ·
mvader (Victron Energy) avatar image mvader (Victron Energy) ♦♦ commented ·
Hi @N-DEE , thank you. noted and we'll check and get back to you. I see that you were also in touch with @Daniël Boekel (Victron Energy Staff) earlier.
0 Likes 0 ·
n-dee avatar image n-dee mvader (Victron Energy) ♦♦ commented ·

Thanks.

Yes that was because of high fluctuations. But now grid setpoint is not met most of the time.
But water warming and charger enabling depends on that, so for example I had to move the starting-value of water warming further into the minus aswell

Actual grid feed in is slighty better then yesterday - but not -20w
1645476528197.png

0 Likes 0 ·
1645476528197.png (63.9 KiB)
Show more comments
n-dee avatar image n-dee commented ·

In this chart we can see how slowly victron inverters are regulating when there is varying load.
(note - BYD charges so Gridsetpoint is -20 ! Water warming kicks in @ -500w, car charger kicks in on PV -300w so I have to disconnect cars to impede on and off switching)

1646125195642.png

0 Likes 0 ·
1646125195642.png (151.8 KiB)