Hi Techs,
If you program a periodical Generator test run, while the system is connected to the Shorepower, can you switch to use the Generator power?
Shore is on AC1IN
Gen is on AC2IN
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Hi Techs,
If you program a periodical Generator test run, while the system is connected to the Shorepower, can you switch to use the Generator power?
Shore is on AC1IN
Gen is on AC2IN
If you switch your inputs around then the inverter will ignore shore power on AC2 in favor of AC1 power (generator)
If both are connected the system will always use AC IN 1. To use AC IN 2 you need to disconnect AC IN 1 or you give a signal to the Quattro and program it to ignore AC IN 1 in that case.
But the easiest way would be to just swap them. What do you think is the problem with that in normal operation?