Help with Fronius Symo 15kW 3-phase and Victron MultiPlus II (buckup use) configuration

Hi,

I'm planning a new solar installation on a new house build and was hoping someone could please help me determine the best way to plan and configure it. If I plan to install a 3-phase Fronius Symo 15kW inverter, does that mean I could install 1x Victron MultiPlus II 5000VA units connected to L1 phase?

This is the configuration I thought would work best but I'd really appreciate help on whether this configuration is valid and if anyone has thoughts on this design?


Many thanks in advance.

17.jpg

Multiplus-II
17.jpg (95.9 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Rob Duthie avatar image
Rob Duthie answered ·

Hi

That should be OK, i believe you are using Victron Cerbo or CCGX controller for the ESS system control?

Regards

Rob D

NZ

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

virusvitamin avatar image
virusvitamin answered ·

Hi

Thank you.

I am planning to use a Victron Cerbo controller and controll panel GX Touch 50 to control system.

Regards

Konstantin

Ukraine

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Rob Duthie avatar image Rob Duthie commented ·
Hi Konstantin

Thats OK, you know with the Victron you can export excess DC power from the MPPT once the batteries are full and the house loads are supplied.

You may need a Current meter ET112 on that L1 phase to have control over current flows etc. Unless you are not going to export surplus power?

My wife is from Ukraine and still has family in Keiv and Dnipro.

Regards

Rob D