question

richard-blaauw avatar image
richard-blaauw asked

Is the VE.Bus BMS compatible with a Phoenix Combi 12/1600/75

I'm looking at upgrading our boats electrical system to a LiFePO4-based system. As far as the components go, I'm pretty sure I have the configuration figured out. The only thing I cannot determine, is whether our current Victron Phoenix Combi 12/1600/75 Inverter/Charger is compatible with the VE.Bus BMS. The setup I am thinking about is very similar to the example given in the VE.Bus BMS manual, shown below. Can we use our Phoenix Combi in this setup?


BMSchargerPhoenix InverterVE.Bus
system-schematic.png (252.8 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
boekel avatar image
boekel answered ·

Am I correct in thinking this is a very old unit without VE.bus connection?
if so then no, as far as I know there is no remote input to switch charger / inverter on/off.

4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

richard-blaauw avatar image richard-blaauw commented ·

@Boekel: Indeed, it is an older unit. I believe it is from 2004. But it does have a databus for an 8-pin UTP connector, with which it is currently connected to a Phoenix Multi Control panel. The manual refers to this RS485 communication as "Victron Information Protocol".

Furthermore, the manual also suggests that there is a remote switch possibility. Below I have copied an image from the (dutch) manual to clarify. The serial databus is on the top left, the remote switch connector is indicated.

Is there a way to use this unit in the setup I have in mind?


0 Likes 0 ·
phoenix-combi.png (37.3 KiB)
boekel avatar image boekel ♦ richard-blaauw commented ·

you could use 2x relay driven by the bms to emulate the remote switch.

a couple of things:
-when inverter is 'on' it still charges, so you'll have to wire so that when 'charge enable' is off, the inverter is switched off.

-your remote control panel probably can't be combined with this

-if the bms shuts down the combi due to low battery, the combi (and bms, and relay) will still use a little power and empty the battery, so make sure you configure the combi in a way that it shuts down on low voltage when there is still enough capacity left in the battery.

0 Likes 0 ·
Tobias avatar image Tobias richard-blaauw commented ·

Hello @Richard Blaauw

I apologise for hijacking this rather old topic, but I’m really interested in your setup with connecting a Phoenix Combi to a Phoenix Multi Control Panel. I have not been able to get verification by anyone at Victron that this combo actually works. Is it the 200/200A GX or is it the 200/200A panel?

Do you get the full functionality of the panel, or is it a reduced set of functions when connected to the Phoenix Combi?



0 Likes 0 ·
Show more comments
ur12vman avatar image
ur12vman answered ·

From scanning the phoenix combi manual here: https://www.victronenergy.com/Manuals/phoenix%20combi/PhoenixCombiUKPc00170e-rev01(1).PDF

I see no provisions for the proper charge algorithm for LiFePo4 batteries, without the proper algorithm you are most likely going to damage Li batteries. The combi also does not have a VE Bus provision. Time to upgrade.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.