24/300 Phoenix Inverter shut down with ripple too high (4 Volts ripple) at battery terminals. Corrected to 2 Volts ripple. Is it safe to re.connect?

input current
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Guy Stewart (Victron Community Manager) avatar image
Guy Stewart (Victron Community Manager) answered ·

Even 2V is high, what is causing this?

Is the inverter very far from the batteries with tiny wires?

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

geomz avatar image geomz commented ·

Exactly what I was thinking.

Plus he mentions the inverter is currently off, so what's generating a 2v ripple with the AC/DC source off?

Do you have some other charger(s) on the system?

How did you "correct" for the 4v ripple? Which BTW is... wow :)

Best bet is to disconnect as many "extra" components as possible and work backward from the inverter and battery being the only two objects connected together, with confirmed good solid sufficiently sized wiring, and then start adding bits and pieces.