Configure Quattros for 2 phase operation.

Can someone tell me if two of quattros can be used together for 2 phase opperation. I have seen much about three phase but nothing about two phase.

quattro 10kva
6 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

sunshinepower avatar image sunshinepower commented ·

Hello, this is my first post.

I have 2 quattros 10kva, and I have 2 phase power on property, Can the 2 quattros be used together one on each phase with common neutral (as three phase would be connected) only two phases with two inverters.

Thanks

0 Likes 0 ·
Alexandra avatar image Alexandra ♦ sunshinepower commented ·
@sunshinepower

As in split phase like America?

Or two of three phases to have backup power?

You can have one inverter on each phase running as a separate system.

Two inverters sharing one battery bank is a whole other issue and not supported.

0 Likes 0 ·
sunshinepower avatar image sunshinepower Alexandra ♦ commented ·
I am in Australia, two phase not split, I have two phases not three. This is how the property is wired up, Two phases with a neutral. I have different appliances running off each of the two phases, 240v on each phase. And yes I also have batteries and they need to be incorporated into the system they are 48v lithium, I have 6 of them, Around 19kwh all together. I thought I had seen in videos with three phase systems with batteries as part of the system.

Is it impossible to have a 2 or 3 phase system sharing the same battery bank?

Do the batteries have to be broken up into two or three separate banks depending on if you are using three inverters for three phase or two inverters for two phase?

Thank you for your help. Greatly appreciated.


0 Likes 0 ·
snoobler avatar image snoobler Alexandra ♦ commented ·

@Alexandra


Please clarify "Two inverters sharing one battery bank is a whole other issue and not supported."


Victron schematic clearly shows a single battery bank powering two Quattros in split phase:


https://www.victronenergy.com/upload/documents/Split-Phase-Quattro-system-with-Cerbo-GX-Touch-50-Discover-42-48-6650-Smart-solar-MPPT's.pdf

0 Likes 0 ·
Alexandra avatar image Alexandra ♦ snoobler commented ·
@snoobler

Two inverters configured as a split phase is one system.

I am referring to hanging two inverters up and electrically connected to one bank. That is not one system but two inverters with a shared battery.

0 Likes 0 ·
sunshinepower avatar image sunshinepower snoobler commented ·
This diagram shows a split system, I am wanting a two phase system. Both systems use two inverters but are different. I have not seen anything that comes from victron that shows a two phase system setup.
0 Likes 0 ·
2 Answers
wkirby avatar image
wkirby answered ·
I think there has mostly been a misunderstanding of the question. I initialy thought you has three phase but wanted to only use two.


So if you only have two phases which are 120° / 240° then it is possible to have two Quattros in a system like this. The two Quattros can be configured as a two phase system with 120° / 240° phase separation.
Both of these Quattros configured as a two phase system MUST share the same battery bank, do not split the battery bank.

12 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

sunshinepower avatar image sunshinepower commented ·
Thats good to know, I am glad you can see how I want the set up to be now. However I am not sure what the phase separation is from the grid, I would presume it is 120 / 240, Are there instructions on how to do this?
0 Likes 0 ·
bbmz avatar image bbmz sunshinepower commented ·
You need to be sure about this - this detail is very important. Probably talk to an electrician in your area.


Do you have your own transformator with two phases and one middle potential (SWER)? Or do you have a (normal) grid connection to a three-phase grid (but for whatever reason no connection to the third phase)? Both systems exist in Australia …


What @wkirby is referring to is the angle between the phases. In a three-phase system (where you can e.g. connect huge motors directly) there is a constant phase angle of 120 degree between the phases (e.g. Europe). In an split-phase system, the two phases are separated by an angle of 180 degrees.

0 Likes 0 ·
sunshinepower avatar image sunshinepower bbmz commented ·

This is the transformer that supplies my property.20220118-140851.jpg

0 Likes 0 ·
Show more comments
PeterM avatar image
PeterM answered ·

Can one implement a split phase system with 0 deg phase angle - basically two quattros are in phase with each other but not in parallel. I would like to do this in an offgrid dual redundant system where a device selects AC from one and switches to other if that one fails ,however only having one common battery bank