Can someone tell me if two of quattros can be used together for 2 phase opperation. I have seen much about three phase but nothing about two phase.
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Can someone tell me if two of quattros can be used together for 2 phase opperation. I have seen much about three phase but nothing about two phase.
Hello, this is my first post.
I have 2 quattros 10kva, and I have 2 phase power on property, Can the 2 quattros be used together one on each phase with common neutral (as three phase would be connected) only two phases with two inverters.
Thanks
As in split phase like America?
Or two of three phases to have backup power?
You can have one inverter on each phase running as a separate system.
Two inverters sharing one battery bank is a whole other issue and not supported.
Is it impossible to have a 2 or 3 phase system sharing the same battery bank?
Do the batteries have to be broken up into two or three separate banks depending on if you are using three inverters for three phase or two inverters for two phase?
Thank you for your help. Greatly appreciated.
Please clarify "Two inverters sharing one battery bank is a whole other issue and not supported."
Victron schematic clearly shows a single battery bank powering two Quattros in split phase:
https://www.victronenergy.com/upload/documents/Split-Phase-Quattro-system-with-Cerbo-GX-Touch-50-Discover-42-48-6650-Smart-solar-MPPT's.pdf
Two inverters configured as a split phase is one system.
I am referring to hanging two inverters up and electrically connected to one bank. That is not one system but two inverters with a shared battery.
So if you only have two phases which are 120° / 240° then it is possible to have two Quattros in a system like this. The two Quattros can be configured as a two phase system with 120° / 240° phase separation.
Both of these Quattros configured as a two phase system MUST share the same battery bank, do not split the battery bank.
Can one implement a split phase system with 0 deg phase angle - basically two quattros are in phase with each other but not in parallel. I would like to do this in an offgrid dual redundant system where a device selects AC from one and switches to other if that one fails ,however only having one common battery bank
Additional resources still need to be added for this topic
28 People are following this question.