Problem setting up wanted configuration

Hello,

I have 3 MultiPlus-II 48/3000/35-32 with firmware 477 and identifification 2629

BYD Premium LV battery

5kW in panels and smartsolar mppt

and not allowed to feedback in grid.


I was trying to setup 3-phase system, connected to grid only on demand of higher loads or battery less than 30%.

I already tried virtual switch, with only one value of higher load than a number, but it was not connecting to grid, but because of higher load, system was shutting down.


I tried HUB-1 but again, without success, it is only in mode only charger, I dont why, here is the setup:hub1.png

I tried also this:

https://www.victronenergy.com/live/assistants:ignore_ac_input_using_the_generator_assistant

and this:

https://www.victronenergy.com/live/assistants:overview_of_available_assistants#deprecated_self-consumption_hub-2_v3_-_for_ac-coupled_systems

Non of these was doing what I expected.

I dont know what else to try. I have 2 other installation working correctly but with older CPUs and firmware on multiplus with HUB-1 assistant ...


Thank you for any suggestion


Multiplus-II
hub1.png (26.2 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Alexandra avatar image
Alexandra answered ·

@asimko@kits.sk

Not sure if you have decent contactors available to you, but you can also use the gx relay with generator setup and contactors to disconnect grid as needed.

6 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

asimko avatar image asimko commented ·

Ok lets say that is a option,but this installation is far from me, and i have 2 identical installations but with older multis and now it does not work? there must be a setup alternative or isnt it? with newer firmware i cannot do what i was able before?